Turbine flowmeter installation precautions

Time: 2020-02-20 12:02:50 Click:0
Turbine flowmeter installation precautions is following:

(1) Installation site
The turbine flowmeter sensor should be installed in a place where maintenance is easy, and the pipeline is free from vibration, strong magnetic interference and heat radiation. When installed outdoors, there should be measures to avoid direct sunlight and rain.
(2) Installation requirements and precautions
The sensor installed horizontally of the turbine flowmeter requires that the pipeline should have no observable tilt (within 5 deg;). The vertical deviation of the sensor installed vertically should be less than 5 deg;, and the fluid direction should be downward and upward.
Where the flow cannot be stopped, bypass and stop valves should be installed.
If the fluid contains impurities, a filter should be installed on the upstream side; if it contains gas, a deaerator should be installed on the upstream side. The drain and air outlet of the filter and the air cleaner should lead to a safe place.
The flow regulating valve should be installed downstream of the sensor, and the upstream shut-off valve should be fully opened during measurement, and must not cause vibration and external leakage. For processes that may produce reverse flow, check valves should be added to prevent reverse flow of fluid.
The sensor should be concentric with the pipeline, and the sealing gasket must not protrude into the pipeline. The sensor should no longer be at the high point of the pipeline, so as to prevent the gas accumulated in the pipeline (such as air mixed in when the flow is stopped) staying at the sensor, which is difficult to discharge and affect the measurement.
The pipes at the front and rear of the sensor should be supported firmly without vibration. For condensable fluids, heat insulation measures should be taken for the sensor and its front and rear pipes.
Transmission cables are usually two-core or three-core with shielded signal cables. The shielded signal cables should be grounded at the end of the display instrument (flow totalizer or flow calculation controller). The transmission path should not be parallel to the power supply line. Area where lines are concentrated.
Turbine flowmeter installation precautions
Article from:yibiaohui

TheTurbine flowmeter is one of the main products of the NOIKE. For more information, please visit the product page orZANKE staff.
主站蜘蛛池模板: 一级毛片完整版免费播放一区 | 国产精品久久久影院 | 国金国银| 苍井空三点高清线视频 | 日本一区二区三区视频在线观看 | 国产乱妇乱子在线视频 | 久久精品视在线-2 | 日韩精品在线视频观看 | 日本少妇按摩做爰2 | 久草这里只有精品 | 在线va无卡无码高清 | 色99视频| 无码一卡二卡三卡四卡 | 久re这里只有精品最新地址 | 浪潮AV在线观看高清 | 小蝌蚪APP丝瓜无限看下载 | 有人有片资源吗在线观看WWW视频 | 免费黄色网址入口 | 国产亚洲精品久久播放 | 精品视自拍视频在线观看 | 久久久精品免费热线观看 | 久久久日韩成人精品电影 | 亚洲精品无码一二区A片 | 婷婷综合亚洲爱久久 | 97色伦图区97色伦综合图区 | 性色AV无码成人亚洲一区 | 污视频app破解下载 污视频app网址丝瓜视频 | 国产露脸无码A区久久 | 日韩AV免费一二三区视频 | 国产亚洲精品久久久性色情软件 | 亚欧美综合 | 亚洲欧洲中文日韩久久AV乱码 | 动漫精品欧美一区二区三区 | 国产精品久久久久久久久夜色 | 一区三区三区不卡 | 先锋影音波波资源网 | 欧美日韩在线视频免费完整 | 能看的黄色网址 | 国产精品户露AV在线户外直播 | 亚洲免费视频日本一区二区 | 女人毛毛扒开自慰 |