Professional Installation Guide for NFS22 Series Mechanical Flow Switches?
I. Pre-Installation Preparation?
Pipe Section Selection?
Select horizontal or vertically upward-flowing straight pipe sections (inverted installation PROHIBITED)
Ensure upstream/downstream straight pipe sections ≥5× pipe diameter; avoid turbulence sources (elbows, valves, etc.)
Clean pipeline interior to prevent paddle obstruction
Flow Direction Calibration?
Confirm medium flow direction strictly matches the arrow indicator on the switch housing
II. Mechanical Installation Procedure?
Threaded Connection? (DN20/DN25 interfaces)
Wrap PTFE thread seal tape or apply sealant to external pipe threads
Hand-tighten the switch into pipe internal threads, then secure with a wrench for additional 1/4 turn (AVOID over-tightening to prevent housing deformation)
Paddle Positioning?
Paddle axis must be parallel to pipeline centerline
Adjust insertion depth to ensure paddle remains suspended without contacting pipe walls/throttling elements
III. Electrical Wiring Specifications?
Safety Operations?
Disconnect power and verify de-energization before wiring
Use ONLY designated equipment grounding terminal for grounding
Terminal Functions?
Terminal Function Wire Color Example
COM Common Terminal Yellow/Grey
NO Normally Open (flow ON) White/Orange
NC Normally Closed (flow OFF) Black/Blue
? Wiring Example?:
Flow Protection: NO terminal → Equipment start/stop control circuit, COM terminal → Power supply positive
IV. Commissioning & Verification?
Flow Setting?
Rotate adjustment knob clockwise to increase trigger flow, counterclockwise to decrease (accuracy: ±2%)
Recommended setting range for fire protection systems: 1~3.5L/s
Functional Testing?
No-flow Test?: When flow drops below 10% of setpoint, NC contacts should CLOSE
Full-flow Test?: When flow reaches setpoint, NO contacts must OPEN immediately (pressure loss ≤0.01bar)
V. Prohibited Actions? ??
DO NOT install inverted or with paddle contacting pipe walls
NEVER wire under power or adjust non-calibration screws
AVOID installation near vibration sources (pumps/compressors)
Note: For hydraulic systems, post-installation testing must evaluate lubricating oil film's impact on paddle sensitivity.
(This translation preserves all technical specifications, safety protocols, and industry terminology from the original Chinese documentation.)